Replies: 2 comments 8 replies
-
(How) can I use the SG-Ready functionality of the Buderus HM200 hybrid manager ? |
Beta Was this translation helpful? Give feedback.
-
Hello, I want to read (and wish to write) the SG-Ready mode. I'm now able to read the mode via:
This is probably the end of the journey of writing the SG Ready Mode 1..4 via software or hardware (BBQKees Gateway S3 on the Buderus HM200.2). But reading of the current Mode SG Ready Mode is possible (see screenshots). |
Beta Was this translation helpful? Give feedback.
-
I want to improve the energy management of the following hybrid installation:
In general I use the "cost optimized" hybrid strategy of the HM200. With 11ct gas and 37ct electricity costs the HM200 choose the heatpump on +2°C and higher and the gas boiler below +2°C.
Now I use the electricity of my PV to feet the heatpump also on temperatures lower than +2°C. Therefore I implement the following energymanagement strategy in node red and inject the parameter into the system with ems-esp commands:

The result of the last 2 days is:

Now my question to you:
Has anybody an easier/better strategy ? Or other ideas to implement an energymanagement for a hybrid system ?
Beta Was this translation helpful? Give feedback.